I looked at the link again.
Basically IF you have an " equipment grounding " conductor run from the house to the garage/shop in the main feed 'marrying' the neutral and ground in the garage/shop panel is not necessary. It's already done in the main panel at the house.
Look at the two attached pics. Notice they show 4 conductors coming into the subpanel from the house, subpanel ground and neutral are NOT 'married", however the main panel in the house shows them 'married'.
ALSO - the Notes they refer to in those images are not the same note I posted earlier. Each image has its own set of applicable notes.
Basically IF you have an " equipment grounding " conductor run from the house to the garage/shop in the main feed 'marrying' the neutral and ground in the garage/shop panel is not necessary. It's already done in the main panel at the house.
Look at the two attached pics. Notice they show 4 conductors coming into the subpanel from the house, subpanel ground and neutral are NOT 'married", however the main panel in the house shows them 'married'.
ALSO - the Notes they refer to in those images are not the same note I posted earlier. Each image has its own set of applicable notes.