i thought i would try posting again as everyone was such a good help last time. I ended up going with Lincoln 256 because i found one a really good deal locally. I have been using for a few months without any issues and am loving it, but recently the 50 amp breaker on the panel has been tripping regularly. It is an older breaker and i am sure that it time to replace it. My question is since i am buying a new breaker anyway should i replace with another 50 amp breaker or should i put a 60 amp breaker in. Thanks all.
Announcement
Collapse
No announcement yet.
Breaker size needed
Collapse
X
-
What size wire is on the entire circuit, and how long from welder to panel? Copper or aluminum? Is it a dedicated circuit? Commercial or residential setting? What voltage? Is the receptacle dedicated for welder use or is it possible that something else can be plugged into it?
How hot are you running it? At its rated output of 250A, it's drawing less than 52A on a 240V circuit, especially at a welder's usually low duty cycle. Granted, you might be pushing 300A if you are doing the big stuff the machine can do, and then, yeah, it's gonna suck juice during arc-on. Do you have a clampmeter to test the actual draw going through the breaker?Last edited by MAC702; 12-16-2016, 05:30 PM.
- Likes 1
-
Originally posted by MAC702 View PostWhat size wire is on the entire circuit, and how long from welder to panel? Copper or aluminum? Is it a dedicated circuit? Commercial or residential setting? Is the receptacle dedicated for welder use or is it possible that something else can be plugged into it?
To to be honest safest bet is to put a 50amp back. That welder only draws 52amps max per the spec sheet. And that's running wide open at 300amps of output. That's a lot and more then likely your nowhere near that kinda output long enough to trip the breaker.
Try a new breaker first. It's always going to be the cheapest thing to do if you don't have something else on the same circuit as MAC702 pointed out.
- Likes 1
Comment
-
Originally posted by Lostone View Post
...That welder only draws 52amps max per the spec sheet. And that's running wide open at 300amps of output. ...
Comment
-
Originally posted by MAC702 View Post
Well, the 52A draw is at rated output of 250A. Max output is 300A and will have more draw. But drop the numbers a tiny bit if on a true 240V American circuit. Raise significantly if on a 208V leg of a three-phase wye service.
Its actually 56A @ 208 volts / 52A @ 230 Volts st the rated 250 amps. But the voltage starts dropping fast after 250 amps. The also list a recommended breaker size of 60 amps.
I wonder if there isn't a voltage drop issue?
Comment
-
Originally posted by Farmer Marty View PostThanks for all replies. Here is more info. Panel is a Siemens. Wire is a 4 guage copper and is new. I just replaced it a year ago. Distance is 10 feet.
An aside--It's going to be interesting when the 2017 code comes out; I understand it adds a requirement to use calibrated torque wrenches (and I assume screwdrivers) for all connnections; how does the inspector check for that? Do they have to watch you make all the connections in the building? Or do you just show them you have the tools? Anxious to see how it plays out.
Comment
-
Originally posted by Aeronca41 View Post
An aside--It's going to be interesting when the 2017 code comes out; I understand it adds a requirement to use calibrated torque wrenches (and I assume screwdrivers) for all connnections; how does the inspector check for that? Do they have to watch you make all the connections in the building? Or do you just show them you have the tools? Anxious to see how it plays out.
My thought was they would have to show the tools, but knowing electricians I've worked with in the past, very few would take the time to used it.
Comment
-
Originally posted by Lostone View Post
I asked one of the building inspectors at work. He said that they could spot check a few, but that didnt show it they were over tightened.
My thought was they would have to show the tools, but knowing electricians I've worked with in the past, very few would take the time to used it.