Miller spot welder LMSW-52 with timer 230V 2.5kva plug rating?

Collapse
X
 
  • Filter
  • Time
  • Show
Clear All
new posts

  • Miller spot welder LMSW-52 with timer 230V 2.5kva plug rating?

    What type of plug comes with this welder? The manual says tandem plug. Is this a 20amp or 30amp plug?

  • #2
    Please post the serial number so we can look it up.

    Comment


    • #3


      Not much help though.

      The specs state 2.5KVA 30amps 10g power cord so I'm guessing a 6-30p is on the machine.




      Ed Conley
      http://www.screamingbroccoli.net/
      MM252
      MM211
      Passport Plus w/Spool Gun
      TA185
      Miller 125c Plasma 120v
      O/A set
      SO 2020 Bender
      You can call me Bacchus

      Comment


      • #4
        Agree. There is a picture of the timer plug on page 23 of the manual and it sure looks like a 6-30p.

        Comment


        • #5
          The plug on the spot welder fits a 6-20p. I did some searching and found this interesting thread. I don't like it that I would need to install a 20amp outlet on a 30amp breaker. That seams it is against code. This thread addresses the issue but I'm not sure how to move forward. I thought maybe someone changed the plug but that seams not to be the case.

          http://www.tractorbynet.com/forums/r...tml#post229893

          Comment


          • #6
            See NEC (NFPA 70) Article 630. Special rules for welders.

            Comment


            • #7
              I'm going to install a 20amp breaker and 6-20P outlet for 220V. The welder will be over protected. It may trip the breaker at times.

              Comment


              • #8
                That is obviously perfectly safe. Please let us know how many nuisance trips you get if any.