I bought an old Dialarc HF welder and am giving a good going-over, including paint and decals. Where I am at now is with the input wiring. This welder does not have power factor correction and at 230V has a max input of 90 amps.
Let me back-up a bit. What I really had in mind to buy was something like a Thunderbolt XL or a Lincoln 'tombstone type' AC/DC, but for half the cost, I found this machine - about $250ish w/running gear, tig foot pedal and regulator. BTW, my Wife fussed that I had brought home something else to trip over in the basement, but I said, I don't think anyone's going to trip over this machine
About 500lbs!
I doubt I'd ever need the full capacity of this machine - more along the requirements of one of the buzz boxes I mentioned above.
I want to be in compliance with code and I think that can go smaller with the input amps providing I provide proper wiring and protection at a reduced amperage. For example, if I size the input wire and breaker for 50 amps, then I am more conservative than NEC recommends for this machine.
That brings me to my question. It would be nice to wire this thing to a 50 amp circuit where I can simply plug it in - unplug and take to my Dad's house if required for a welding chore. That's what I'd do with a buzz box.
My question is - what are your opinions of this route and how much am I limiting the capabilities of this machine (or causing unintended damage) by going with a 50 amp circuit?
Thanks in advance,
Bill
Let me back-up a bit. What I really had in mind to buy was something like a Thunderbolt XL or a Lincoln 'tombstone type' AC/DC, but for half the cost, I found this machine - about $250ish w/running gear, tig foot pedal and regulator. BTW, my Wife fussed that I had brought home something else to trip over in the basement, but I said, I don't think anyone's going to trip over this machine

I doubt I'd ever need the full capacity of this machine - more along the requirements of one of the buzz boxes I mentioned above.
I want to be in compliance with code and I think that can go smaller with the input amps providing I provide proper wiring and protection at a reduced amperage. For example, if I size the input wire and breaker for 50 amps, then I am more conservative than NEC recommends for this machine.
That brings me to my question. It would be nice to wire this thing to a 50 amp circuit where I can simply plug it in - unplug and take to my Dad's house if required for a welding chore. That's what I'd do with a buzz box.
My question is - what are your opinions of this route and how much am I limiting the capabilities of this machine (or causing unintended damage) by going with a 50 amp circuit?
Thanks in advance,
Bill