Announcement

Collapse
No announcement yet.

Multimatic 200 amperage question

Collapse
X
 
  • Filter
  • Time
  • Show
Clear All
new posts

  • L1BR8-TED
    replied
    Thanks for the clarification guys. I appreciate it.

    Leave a comment:


  • H80N
    replied
    The 6-50 has pretty much become the defacto standard for single phase welder hookup....

    Go ahead and use the one supplied... with the MVP...it has ample capacity for your Multimatic...

    SEE 5-8. Multi−Voltage Plug (MVP) Connection Page 27 of the PDF

    https://www.millerwelds.com/files/ow...53392J_MIL.pdf


    .


    Last edited by H80N; 01-07-2016, 07:19 AM.

    Leave a comment:


  • xryan
    replied
    The machine recommends a 25 amp 230 volt circuit, so If you plug it into 6-50R (receptacle) you have 50 amps available if it is wired correctly to the branch circuit... So you could run two machines plugged into the same circuit with 2 6-50R outlets... The machine comes with a 6-50P (plug).

    Leave a comment:


  • L1BR8-TED
    started a topic Multimatic 200 amperage question

    Multimatic 200 amperage question

    I recently purchased a Multimatic 200. I'm curious to know if I can connect this welder to a nema 6-50R connection that is rated at 50 amps safely. I've read different things online and in the manual. The manual states "Recommended Standard fuse rating in amperes at 25 amps" on page 5-9. But I've also read on the online multimatic 200 pdf "Multi-voltage plug (MVPTM) allows you to connect to common 120 or 230 V power receptacles without the use of any tools — choose the plug that fits the receptacle and connect it to the power cord. " "
    -Power cord and MVP plugs 5-15P (115 V, 15 A) and 6-50P (230 V, 50 A)
    ​I would like to safely hook it up to a 50 amp receptacle because in the future there is a possibility that I may upgrade to a larger machine that would require more amperage.
    Any info would be appreciated.






Working...
X
😀
🥰
🤢
😎
😡
👍
👎