INTP - 20 Amp plug, 30 amp breaker??
That is A Bad Ideatm
If you really have a problem with the air compressor tripping the breaker on startup, go to a 20 amp slow blow breaker. If you want to use a 30 amp breaker, you MUST use a plug rated at 30 amps minimum.
Anything else is folly.
Sure, you can get away with it for a while. The NEC has a bit of slack built into it to allow for transient loads and natural variabilty. Responsible manufacturers put in a factor of safety because of variations in quality and to allow for end user error. One person, with one receptacle, can beat the odds temporarily.
One thousand people, each with one receptacle, will experience fires and shorts.
Sure, you know that the socket you labeled "30 amp" is a 20 amp socket. When you sell, will the next owner of the shop know? Will you remember to change the breaker, the receptacle, or the label before leaving? When a fire starts because he plugs in a 30 amp load, you will be at fault.
Look at the fire this weekend on a Canadian submarine fresh out of refurbishing. One officer died and at least six are seriously injured due to an electrical fire that started in one subpanel, spread to the main panel, and knocked out power to the entire boat. Millions of dollars damage, and hte investigation is just starting.
If the breaker is tripping, and it is the recommended size, find out why. Don't just flip a bigger breaker in and assume the problem is solved.
Finally, if you suggest someone else follow NEC and NEMA spec, don't turn around and tell them that you are disregarding it.
Respectfully
Karl
That is A Bad Ideatm
If you really have a problem with the air compressor tripping the breaker on startup, go to a 20 amp slow blow breaker. If you want to use a 30 amp breaker, you MUST use a plug rated at 30 amps minimum.
Anything else is folly.
Sure, you can get away with it for a while. The NEC has a bit of slack built into it to allow for transient loads and natural variabilty. Responsible manufacturers put in a factor of safety because of variations in quality and to allow for end user error. One person, with one receptacle, can beat the odds temporarily.
One thousand people, each with one receptacle, will experience fires and shorts.
Sure, you know that the socket you labeled "30 amp" is a 20 amp socket. When you sell, will the next owner of the shop know? Will you remember to change the breaker, the receptacle, or the label before leaving? When a fire starts because he plugs in a 30 amp load, you will be at fault.
Look at the fire this weekend on a Canadian submarine fresh out of refurbishing. One officer died and at least six are seriously injured due to an electrical fire that started in one subpanel, spread to the main panel, and knocked out power to the entire boat. Millions of dollars damage, and hte investigation is just starting.
If the breaker is tripping, and it is the recommended size, find out why. Don't just flip a bigger breaker in and assume the problem is solved.
Finally, if you suggest someone else follow NEC and NEMA spec, don't turn around and tell them that you are disregarding it.
Respectfully