Hey guys, newbie here.
Have done some searching/asked a friend so I'm not at a COMPLETE loss. Anyway:
My current set up is a 200A input breaker into my panel. From that, there's 8 spots for breakers, all of which are full. In particular, I'm running my MIG on a 50A breaker, runs ~15' to a "dryer style" 3 prong plug, via #10 wire. I'd now like to add in the Syncrowave 250. My plan is to:
Pull the 50A breaker, replace w/ 100A. Change #10 wire to #6. (NEC question: Can I run it in the existing 3/4" metal conduit? Or is it time to bump that up in size?). This run will go to a sub panel, which contains the 50A breaker I replaced, and a lead back out to my outlet to run the MIG. I will NEVER be using BOTH welders at the SAME time. I will then be wiring in my syncro 250 at the sub panel. That's where my question comes in: can I wire it in here as a plug, so that I can move the unit around? Or is hardwiring the only "good" choice? Maybe a 6/3 extension cord hard wired in is what I'm after? I'd like to be able to roll it out into the carport area, about 25' away, (welder is on a cart, too) and tackle some on-vehicle welding if needed.
Anyway, if someone could eye-over my intended setup and tell me "good to go" or "do this instead" that would be awesome!! Planning to tackle this tomorrow AM.
Thank you all!!
Have done some searching/asked a friend so I'm not at a COMPLETE loss. Anyway:
My current set up is a 200A input breaker into my panel. From that, there's 8 spots for breakers, all of which are full. In particular, I'm running my MIG on a 50A breaker, runs ~15' to a "dryer style" 3 prong plug, via #10 wire. I'd now like to add in the Syncrowave 250. My plan is to:
Pull the 50A breaker, replace w/ 100A. Change #10 wire to #6. (NEC question: Can I run it in the existing 3/4" metal conduit? Or is it time to bump that up in size?). This run will go to a sub panel, which contains the 50A breaker I replaced, and a lead back out to my outlet to run the MIG. I will NEVER be using BOTH welders at the SAME time. I will then be wiring in my syncro 250 at the sub panel. That's where my question comes in: can I wire it in here as a plug, so that I can move the unit around? Or is hardwiring the only "good" choice? Maybe a 6/3 extension cord hard wired in is what I'm after? I'd like to be able to roll it out into the carport area, about 25' away, (welder is on a cart, too) and tackle some on-vehicle welding if needed.
Anyway, if someone could eye-over my intended setup and tell me "good to go" or "do this instead" that would be awesome!! Planning to tackle this tomorrow AM.
Thank you all!!