    I just bought a new 350 P Aluminum welder, All of the plugs in the shop are 50 amp single phase plugs except for my tig welder that has a big Russel Stoll plug that weighs 20 lbs and is rated for 60 amp 3 phase.

    So my question is: If its rated 60 amps 3 phase that means each prong is rated to carry 20 amps each, however I'm only using 2 prongs because I only have single phase so each prong is now carrying 30 amps at maximum capacity.

    So that has me thinking that the 50 amp single phase plugs are actually rated higher than the 60 amp 3 phase plug I'm using on the tig welder.

    However, if you look at 20 lb Russel stoll aluminum housing plug you would think differently.

    So I'm in a situation where I need a 60 amp single phase plug for the new welder, because I use the welder in different areas of the shop I would rather not have it directly wired into a disconnect.

  • #2
    The plugs are rated based on 100% duty cycle, but welders have much lower duty cycle, especially when the power is turned up all the way. I would just use whatever 50 amp single phase plug you are already using.

    Richard


    Originally posted by Portable Welder View Post
    I just bought a new 350 P Aluminum welder, All of the plugs in the shop are 50 amp single phase plugs except for my tig welder that has a big Russel Stoll plug that weighs 20 lbs and is rated for 60 amp 3 phase.

    So my question is: If its rated 60 amps 3 phase that means each prong is rated to carry 20 amps each, however I'm only using 2 prongs because I only have single phase so each prong is now carrying 30 amps at maximum capacity.

    So that has me thinking that the 50 amp single phase plugs are actually rated higher than the 60 amp 3 phase plug I'm using on the tig welder.

    However, if you look at 20 lb Russel stoll aluminum housing plug you would think differently.

    So I'm in a situation where I need a 60 amp single phase plug for the new welder, because I use the welder in different areas of the shop I would rather not have it directly wired into a disconnect.
    Syncrowave 200, Millermatic 211, Victor torch, Propane forge....

    Comment


    • #3
      Originally posted by raferguson View Post
      The plugs are rated based on 100% duty cycle, but welders have much lower duty cycle, especially when the power is turned up all the way. I would just use whatever 50 amp single phase plug you are already using.

      Richard
      Ditto. I run mine off a 50 amp plug without issue.
      Nothing welded, Nothing gained

      Miller Dynasty700DX
      3 ea. Miller Dynasty350DX
      Miller Dynasty200DX
      ThermalArc 400 GTSW
      MillerMatic350P
      MillerMatic200 with spoolgun
      MKCobraMig260
      Lincoln SP-170T
      Linde UCC305 (sold 2011)
      Hypertherm 1250
      Hypertherm 800
      PlasmaCam CNC cutter
      Fadal Toolroom CNC Mill
      SiberHegner CNC Mill
      2 ea. Bridgeport
      LeBlond 15" Lathe
      Haberle 18" Cold Saw
      Doringer 14" Cold Saw
      6 foot x 12 foot Mojave granite

      Comment


      • #4
        Thanks for your input but I would really like to find the proper plug to run it at max out put if needed.

        Comment


        • #5
          I would think the 60A Russelstoll plug is 60 A per phase.
          Miller stuff:
          Dialarc 250 (1974)
          Syncrowave 250 (1992)
          Spot welder (Dayton badged)

          Comment


          • #6
            Right on

            Originally posted by USMCPOP View Post
            I would think the 60A Russelstoll plug is 60 A per phase.
            USMCPOP is correct. NEMA ratings for connectors are per phase. Your plug is good for 60 amps per pin.

            Comment


            • #7
              "....So my question is: If its rated 60 amps 3 phase that means each prong is rated to carry 20 amps each, however I'm only using 2 prongs because I only have single phase so each prong is now carrying 30 amps at maximum capacity....."

              Not sure what the question is here but each prong of that 3 phase 60A plug is rated at 60A. A device requiring 60A is not expecting 20A on each of the 3 phases but 60A on each phase. And when using single phase, it needs 60A on each of the 2 hot logs - not 30A on each.

              Comment


              • #8
                When we supply a three phase receptacle we divide load between three supply conductors. A 60 amp single phase circuit at 240 volts can supply 14400 watts of power. A three phase circuit uses three windings, but only one more lead. At the same voltage, and amperage the increased power delivered is by a factor of the square root of three or 1.73. 1.73x14400=24912 watts. Ben Franklyn considered electricity to be a fluid. If it were a fluid three pipes would flow 50% more than two. Fluid need not return to the point of origin.

                Oh, a three phase receptacle/plug will work fine on single phase. It will, however present a hazard should someone plug a real three phase load into it.
                Dynasty 280DX
                Bobcat 250
                MM252
                Spool gun
                Twentieth Century 295
                Twentieth Century 295 AC
                Marquette spot welder
                Smith torches

                Comment


                • #9
                  6-50

                  Good.. Bad or Indiferent... the Nema 6-50 is pretty much the De-Facto standard plug for single phase 240 welders..
                  there have been several threads on this subject ...
                  have seen everything from Sync 250 to MM350P...Dyn350... Powermax 1000 etc etc .... in many shops wired with 6-50.. having run for many years with no problems....

                  There seems to be plenty of capacity built into that 6-50 design...
                  rather than the plug being a limiting factor... I believe the rating is keyed to the capacity of the wiring and breaker intended to be supplying it... and if used as intended... you can believe that a receptacle using a 6-50 is wired for at least 50 amps..
                  And yes.. this usage probably defeats the rating system...

                  Oh dear.. here comes a ...Sh.t...Storm...
                  .

                  *******************************************
                  The more you know, The better you know, How little you know

                  “The bitterness of poor quality remains long after the sweetness of low price is forgotten”

                  Buy the best tools you can afford.. Learn to use them to the best of your ability.. and take care of them...

                  My Blue Stuff:
                  Dynasty 350DX Tigrunner
                  Dynasty 200DX
                  Millermatic 350P w/25ft Alumapro & 30A
                  Millermatic 200

                  TONS of Non-Blue Equip, plus CNC Mill, Lathes & a Plasmacam w/ PowerMax-1000

                  Comment


                  • #10
                    The 50A plug will work fine for that machine.

                    Comment


                    • #11
                      Okay then, My 50 amp plug single phase plug that I use on my miller matic 252, MM200 etc. The 50 amp plug is 50 amps per hot leg.

                      Comment


                      • #12
                        okay then looks like I need to buy another Russel stohl plug and run it off that if I want to meet code.

                        Comment


                        • #13
                          Originally posted by Portable Welder View Post
                          okay then looks like I need to buy another Russel stohl plug and run it off that if I want to meet code.
                          You can use the Multiplier to find out if the 6-50 connector will work within code

                          Applies to conductors and connectors.

                          Ed Conley
                          http://www.screamingbroccoli.net/
                          MM252
                          MM211
                          Passport Plus w/Spool Gun
                          TA185
                          Miller 125c Plasma 120v
                          O/A set
                          SO 2020 Bender
                          You can call me Bacchus

                          Comment


                          • #14
                            Thanks for everyone's input.

                            Comment


                            • #15
                              Originally posted by Portable Welder View Post
                              okay then looks like I need to buy another Russel stohl plug and run it off that if I want to meet code.
                              A three phase receptacle, supplied with single phase power does not comply with code.

                              Single phase 60 or 70 amp combos aren't cheap!