What is the amp Draw at 100% duty cycle. Using three phase power will allow you to use smaller conductors for the Line to Load conductors than in single phase.
What is the amp Draw at 100% duty cycle. Using three phase power will allow you to use smaller conductors for the Line to Load conductors than in single phase.
From your 350P handbook
230V 3PH at 60% duty cycle
30 Amps rated input
Breaker normal 35 Amp
Time delay 45 Amp
Minimum conductor size 10 ga.
maximum conductor length 114ft.
minimum ground conductor 10 ga.
I would use the 45 Amp breaker or equivalent time delay slow blow fuses in a fused disconnect.