  • syncrowave 250dx current draw

    Is 90 amp overcurrent protection (breaker) with#4 thhn sufficient for a syncrowave 250dx?

  • #2
    Originally posted by akm06 View Post
    Is 90 amp overcurrent protection (breaker) with#4 thhn sufficient for a syncrowave 250dx?
    Single or three phase?

    On the back of the welder is a table, usually a black label, that tells you the amps at a given voltage.
    Dynasty 280DX
    Millermatic 212
    Spoolgun
    Tools n stuff

    Comment


    • #3
      Originally posted by akm06 View Post
      Is 90 amp overcurrent protection (breaker) with#4 thhn sufficient for a syncrowave 250dx?
      probably a little light on the breaker depending on the input voltage you have it strapped for.....

      take a look at section

      3-19. Electrical Service Guide
      . For 250 DX Models

      page 23 in the manual



      BTW... the Syncrowave is a Single Phase ONLY machine..
      Last edited by H80N; 01-06-2015, 03:01 PM.
      .

      *******************************************