I just bought 304 XMT (230/460v) with feeder and now I need to install a dedicated wiring system for the machine, in garage. Can someone tell/show me what wiring system should look like? Or share a good wiring instruction on here?
The plan is to wire it myself and then have a certified electrician inspect it to make sure everything's safe. I'm taking my time to make sure I understand what I'm working with.
For phase 1 and phase 3, from what I understand, typical home use 1 phase, so I'm going with that.
Here's what I get from the Miller's Manual:
60 Hz Single Phase #1
Input Voltage: 230
Input Amperes At Rated Output: 53
Max Recommendation Standard Fuse Rating in Amperes Time-Delay: 60
Max Recommendation Standard Fuse Rating in Amperes Normal Operating: 80
Min Input Conductor Size in AWK/Kcmil: 8
Max Recommended Input Conductor Length In Feet (Meters): 85 (26)
Min Grounding Conductor Size in AWG/Kcmil: 8
60 Hz Single Phase #2
Input Voltage: 460
Input Amperes At Rated Output: 27
Max Recommendation Standard Fuse Rating in Amperes Time-Delay: 30
Max Recommendation Standard Fuse Rating in Amperes Normal Operating: 40
Min Input Conductor Size in AWK/Kcmil: 10
Max Recommended Input Conductor Length In Feet (Meters): 224 (68)
Min Grounding Conductor Size in AWG/Kcmil: 10
MATERIALS
Time-Delay RK5 fuses rated for 30 or 60amp?
A roll of 8/2 or 10/2 wire?
6-50R receptacle
Line disconnect device/box
Metal junction box for the receptacle
Metal conduit (flexible or rod?)
Other suggestions are welcome.
Thanks
The plan is to wire it myself and then have a certified electrician inspect it to make sure everything's safe. I'm taking my time to make sure I understand what I'm working with.
For phase 1 and phase 3, from what I understand, typical home use 1 phase, so I'm going with that.
Here's what I get from the Miller's Manual:
60 Hz Single Phase #1
Input Voltage: 230
Input Amperes At Rated Output: 53
Max Recommendation Standard Fuse Rating in Amperes Time-Delay: 60
Max Recommendation Standard Fuse Rating in Amperes Normal Operating: 80
Min Input Conductor Size in AWK/Kcmil: 8
Max Recommended Input Conductor Length In Feet (Meters): 85 (26)
Min Grounding Conductor Size in AWG/Kcmil: 8
60 Hz Single Phase #2
Input Voltage: 460
Input Amperes At Rated Output: 27
Max Recommendation Standard Fuse Rating in Amperes Time-Delay: 30
Max Recommendation Standard Fuse Rating in Amperes Normal Operating: 40
Min Input Conductor Size in AWK/Kcmil: 10
Max Recommended Input Conductor Length In Feet (Meters): 224 (68)
Min Grounding Conductor Size in AWG/Kcmil: 10
MATERIALS
Time-Delay RK5 fuses rated for 30 or 60amp?
A roll of 8/2 or 10/2 wire?
6-50R receptacle
Line disconnect device/box
Metal junction box for the receptacle
Metal conduit (flexible or rod?)
Other suggestions are welcome.
Thanks