  • Electric Service Install For Dialarc 250

    My Dialarc 250 is about 130' from the nearest breaker box which is mounted on the power pole. The manual says I can run my input conductor for a maximum of 78' using 8ga wire. I would probably still come up short even using 6ga wire. How do I deal with this?
    I'm thinking I may have to run another service line and breaker box where the welder is.
    Last edited by Hoko; 11-29-2014, 07:24 PM.
    Dialarc 250 AC-DC

  • #2
    Huh? I had 50' of #4 THHN copper on a 100 amp breaker coming from a 200 amp service, it was barely enough. Dialarc 250 is a monster! You could build bridges with it!
    Dynasty 280DX
    Bobcat 250
    MM252
    Spool gun
    Twentieth Century 295
    Twentieth Century 295 AC
    Marquette spot welder
    Smith torches

    Comment


    • #3
      Originally posted by WillieB View Post
      Huh? I had 50' of #4 THHN copper on a 100 amp breaker coming from a 200 amp service, it was barely enough. Dialarc 250 is a monster! You could build bridges with it!
      The specs in the manual call out minimum 70amp breaker @ max 78' feet using 8g wiring.
      Ed Conley
      http://www.screamingbroccoli.net/
      MM252
      MM211
      Passport Plus w/Spool Gun
      TA185
      Miller 125c Plasma 120v
      O/A set
      SO 2020 Bender
      You can call me Bacchus

      Comment


      • #4
        Run heavier aluminum wire and put another box in close to the welder.

        Comment


        • #5
          Originally posted by Country Metals View Post
          Run heavier aluminum wire and put another box in close to the welder.
          Why aluminum?
          Dialarc 250 AC-DC

          Comment


          • #6
            deleted..................
            Last edited by Synchroman; 11-30-2014, 07:49 PM.
            Miller Syncrowave 200
            Milermatic 252
            Lincoln AC/DC "Tombstone"

            Comment


            • #7
              I believe conduit is good workmanship wherever you are. In northern climates I consider it essential. I've never heard of an underground cable failing in summer. I probably average two a year calls from people in January about a cable that has failed underground. In every case they are installed by amateur electricians. It will cost a little more to do it right now, preventing the need to do it again later. I can't understand the obsession with wanting to do it wrong.
              Dynasty 280DX
              Bobcat 250
              MM252
              Spool gun
              Twentieth Century 295
              Twentieth Century 295 AC
              Marquette spot welder
              Smith torches

              Comment


              • #8
                deleted.
                Last edited by Synchroman; 11-30-2014, 07:50 PM.
                Miller Syncrowave 200
                Milermatic 252
                Lincoln AC/DC "Tombstone"

                Comment


                • #9
                  Like WillieB said, a proper install is best the first time.

                  If I am running long distances, I would rather purchase over amp aluminum wire (IE 6ga copper is approx 3 ga aluminum so purchase 1ga or heavier for later demands) and make a new box to box run. It is cheaper, easier to run, but a huge PITA to make connections being so thick.


                  I do this because I never say I just need X amps, and run minimum with copper since it is pricey. Just make sure you follow ALL codes and good wiring practices in doing any work.

                  Common Sense > $$$$ ---- always makes sense.

                  Comment


                  • #10
                    Originally posted by WillieB View Post
                    I believe conduit is good workmanship wherever you are. In northern climates I consider it essential. I've never heard of an underground cable failing in summer. I probably average two a year calls from people in January about a cable that has failed underground. In every case they are installed by amateur electricians. It will cost a little more to do it right now, preventing the need to do it again later. I can't understand the obsession with wanting to do it wrong.
                    In California and other warm states, underground cable is universally used for housing developments. The cables are sticking up from the ground just prior to the foundations being poured.

                    Apparently the builders are obsessed with using underground cable.
                    Miller Syncrowave 200
                    Milermatic 252
                    Lincoln AC/DC "Tombstone"

                    Comment


                    • #11
                      Developers are more concerned with price than durability. Once sold the failure rate isn't their concern. New home buyers seldom know the difference. In a warm climate a failed cable can be dug up any time of year to replace. Of course, with conduit properly installed it won't need to be replaced.
                      Dynasty 280DX
                      Bobcat 250
                      MM252
                      Spool gun
                      Twentieth Century 295
                      Twentieth Century 295 AC
                      Marquette spot welder
                      Smith torches

                      Comment


                      • #12
                        if there is already power to the building you need to upgrade it. 1 power supply to a structure.