  • Electrical connection requirements

    Hello all! I'm not a welder, but an electrician. I have a customer with a MillerMatic 350. We are to connect it to 3 phase 240V. The specs clearly state 30A draw and minimum conductor is #10. The personal at technical support just told me that I should install a 50A breaker and that a 30A safety switch would not be adequate. Am I crazy or does it just seem like he is not understanding or doesn't know. At minimum wire size of #10, a 50A breaker is illegal.

  • #2
    It is allowable due to the machine' duty cycle.

    Normal operating FUSE you would use a 50amp fuse and 10g wire IS MINIMUM
    Wiring following NEC art 630 wiring and that is what they use for the manual.



    Time delay fuse = 30amp rated and 10g wire.

    Ed Conley
    http://www.screamingbroccoli.net/
    MM252
    MM211
    Passport Plus w/Spool Gun
    TA185
    Miller 125c Plasma 120v
    O/A set
    SO 2020 Bender
    You can call me Bacchus

    Comment


    • #3
      Sorry. Disregard. I am not as familiar with Art. 630 than I should be. So I guess the actual question I have is will this welder operate properly connected via 30A non-fuse disconnect, #10 wire
      Last edited by unionsparky; 10-17-2014, 01:30 PM.

      Comment


      • #4
        Originally posted by unionsparky View Post
        Sorry. Disregard. I am not as familiar with Art. 630 than I should be. So I guess the actual question I have is will this welder operate properly connected via 30A non-fuse disconnect, #10 wire
        Are you talking about a normal Circuit Breaker?



        3-phase 240v 30amp CB and 10g wire
        Ed Conley
        http://www.screamingbroccoli.net/
        MM252
        MM211
        Passport Plus w/Spool Gun
        TA185
        Miller 125c Plasma 120v
        O/A set
        SO 2020 Bender
        You can call me Bacchus

        Comment


        • #5
          I believe you can use a overcurrent device up to 200% of the nameplate I1eff, or 200% of nameplate current x multiplier from 630.11(A) What is the duty cycle of the welder?

          It is my opinion that a disconnect switches load only in extreme emergency. Its requirements are the same as the conductors supplying.
          Dynasty 280DX
          Bobcat 250
          MM252
          Spool gun
          Twentieth Century 295
          Twentieth Century 295 AC
          Marquette spot welder
          Smith torches

          Comment


          • #6
            As long as I have the control board set for 230V, will welder care which leg is high leg?

            Comment


            • #7
              I had a similar experience with a Lincoln Power Wave 455... previous owner had it connected to a 120/240 three phase with a high leg. The machine would randomly shut down and the owner just thought it was unreliable. I ran it on a 208 three phase and never had any issue. I think in the previous owner's situation, the wild leg would get outside of the voltage tolerance when other loads in the shop changed, and that's what I figured was going on when I picked up this pulse-spraying beast for a song.

              In this case, I spoke with engineers at Lincoln and they confirmed that the supply voltage was sensed from the L1 and L3 input terminals.

              You might want to give Miller a call and ask them about powering this with unbalanced three phase and see what their engineers say.

              80% of failures are from 20% of causes
              Never compromise your principles today in the name of furthering them in the future.
              "All I ever wanted was an honest week's pay for an honest day's work." -Sgt. Bilko
              "We are generally better persuaded by reasons we discover ourselves than by those given to us by others." -Pascal
              "Since we cannot know all that there is to be known about anything, we ought to know a little about everything." -Pascal

              Comment


              • #8
                Originally posted by Bodybagger View Post
                You might want to give Miller a call and ask them about powering this with unbalanced three phase and see what their engineers say.
                Yeah, working now. They're closed, unless someone has a special number. To be more specific, their service is running ' hot ' at 125V/248V, and 211V high leg. I'm hoping the controls, if derived from 120V are being pulled from A phase. If they are 230V, I hope the welder handles the higher voltage ok.

                Comment


                • #9
                  Originally posted by unionsparky View Post
                  Yeah, working now. They're closed, unless someone has a special number. To be more specific, their service is running ' hot ' at 125V/248V, and 211V high leg. I'm hoping the controls, if derived from 120V are being pulled from A phase. If they are 230V, I hope the welder handles the higher voltage ok.
                  120v Control voltages are supplied from inside the machine via a transformer since there is NO NEUTRAL in the supply circuit.
                  Ed Conley
                  http://www.screamingbroccoli.net/
                  MM252
                  MM211
                  Passport Plus w/Spool Gun
                  TA185
                  Miller 125c Plasma 120v
                  O/A set
                  SO 2020 Bender
                  You can call me Bacchus

                  Comment


                  • #10
                    Well, I decided to put high leg on B phase, white in cord. I saw elsewhere that red is unused for single phase. Meaning that if it has any sensitivity to high leg on A, white must be acceptable. I can't see Miller making equipment that can't be connected to center tapped deltas via single phase.

                    Thanks for all the replies.

                    Comment


                    • #11
                      Delta 120/208/240 Three phase is 240 balanced on three phase. 240 single phase is available from any phase 120 single phase is available from 2 legs to neutral. 208 single phase is available from the high leg to neutral.
                      Dynasty 280DX
                      Bobcat 250
                      MM252
                      Spool gun
                      Twentieth Century 295
                      Twentieth Century 295 AC
                      Marquette spot welder
                      Smith torches

                      Comment


                      • #12
                        If it works on three phase, why not use three phase?
                        Dynasty 280DX
                        Bobcat 250
                        MM252
                        Spool gun
                        Twentieth Century 295
                        Twentieth Century 295 AC
                        Marquette spot welder
                        Smith torches

                        Comment


                        • #13
                          Originally posted by WillieB View Post
                          Delta 120/208/240 Three phase is 240 balanced on three phase. 240 single phase is available from any phase 120 single phase is available from 2 legs to neutral. 208 single phase is available from the high leg to neutral.
                          I'm completely aware of how their service functions. My lack of familiarity is with Miller welders. My question was, if the 208V high leg could damage any control circuits that were expecting to see 120V.

                          Originally posted by WillieB View Post
                          If it works on three phase, why not use three phase?
                          It is connected to 3 phase. I only brought up the 240V single phase scenario as a matter of trying to determine if the equipment would be unhappy with the 208V on a certain leg of the supply. Since the unit is capable of 120V operation, is it entirely possible that the single hot configuration may want only 120V. This would mean that the second conductor used, when connected as single phase 240V would most certainly have to accept 208V on that leg, since I'm sure Miller would not sell equipment that wouldn't have the option to connect single phase 240V to a high leg delta, which could be necessary if the customer has space constraints.

                          It is hooked up and working at 230V 3 phase connection settings.

                          Thanks again everyone!

                          Comment


                          • #14
                            Does the welder connect to neutral? If it does it is the first I've seen connected to neutral. Without neutral there is no high leg. Delta is three transformer windings connected in a triangle diagram. The wild leg or 208 is neutral to the opposite corner of said triangle. Your welder doesn't know about 208.
                            Dynasty 280DX
                            Bobcat 250
                            MM252
                            Spool gun
                            Twentieth Century 295
                            Twentieth Century 295 AC
                            Marquette spot welder
                            Smith torches

                            Comment


                            • #15
                              A Miller Matic 350 connects to 120Volt?
                              Dynasty 280DX
                              Bobcat 250
                              MM252
                              Spool gun
                              Twentieth Century 295
                              Twentieth Century 295 AC
                              Marquette spot welder
                              Smith torches

                              Comment