Hello all! I'm not a welder, but an electrician. I have a customer with a MillerMatic 350. We are to connect it to 3 phase 240V. The specs clearly state 30A draw and minimum conductor is #10. The personal at technical support just told me that I should install a 50A breaker and that a 30A safety switch would not be adequate. Am I crazy or does it just seem like he is not understanding or doesn't know. At minimum wire size of #10, a 50A breaker is illegal.
Announcement
Collapse
No announcement yet.
Electrical connection requirements
Collapse
X
-
It is allowable due to the machine' duty cycle.
Normal operating FUSE you would use a 50amp fuse and 10g wire IS MINIMUM
Wiring following NEC art 630 wiring and that is what they use for the manual.
Time delay fuse = 30amp rated and 10g wire.
Ed Conley
http://www.screamingbroccoli.net/
MM252
MM211
Passport Plus w/Spool Gun
TA185
Miller 125c Plasma 120v
O/A set
SO 2020 Bender
You can call me Bacchus
-
Sorry. Disregard. I am not as familiar with Art. 630 than I should be. So I guess the actual question I have is will this welder operate properly connected via 30A non-fuse disconnect, #10 wireLast edited by unionsparky; 10-17-2014, 01:30 PM.
Comment
-
Originally posted by unionsparky View PostSorry. Disregard. I am not as familiar with Art. 630 than I should be. So I guess the actual question I have is will this welder operate properly connected via 30A non-fuse disconnect, #10 wire
3-phase 240v 30amp CB and 10g wireEd Conley
http://www.screamingbroccoli.net/
MM252
MM211
Passport Plus w/Spool Gun
TA185
Miller 125c Plasma 120v
O/A set
SO 2020 Bender
You can call me Bacchus
Comment
-
I believe you can use a overcurrent device up to 200% of the nameplate I1eff, or 200% of nameplate current x multiplier from 630.11(A) What is the duty cycle of the welder?
It is my opinion that a disconnect switches load only in extreme emergency. Its requirements are the same as the conductors supplying.Dynasty 280DX
Bobcat 250
MM252
Spool gun
Twentieth Century 295
Twentieth Century 295 AC
Marquette spot welder
Smith torches
Comment
-
I had a similar experience with a Lincoln Power Wave 455... previous owner had it connected to a 120/240 three phase with a high leg. The machine would randomly shut down and the owner just thought it was unreliable. I ran it on a 208 three phase and never had any issue. I think in the previous owner's situation, the wild leg would get outside of the voltage tolerance when other loads in the shop changed, and that's what I figured was going on when I picked up this pulse-spraying beast for a song.
In this case, I spoke with engineers at Lincoln and they confirmed that the supply voltage was sensed from the L1 and L3 input terminals.
You might want to give Miller a call and ask them about powering this with unbalanced three phase and see what their engineers say.
80% of failures are from 20% of causes
Never compromise your principles today in the name of furthering them in the future.
"All I ever wanted was an honest week's pay for an honest day's work." -Sgt. Bilko
"We are generally better persuaded by reasons we discover ourselves than by those given to us by others." -Pascal
"Since we cannot know all that there is to be known about anything, we ought to know a little about everything." -Pascal
Comment
-
Originally posted by Bodybagger View PostYou might want to give Miller a call and ask them about powering this with unbalanced three phase and see what their engineers say.
Comment
-
Originally posted by unionsparky View PostYeah, working now. They're closed, unless someone has a special number. To be more specific, their service is running ' hot ' at 125V/248V, and 211V high leg. I'm hoping the controls, if derived from 120V are being pulled from A phase. If they are 230V, I hope the welder handles the higher voltage ok.Ed Conley
http://www.screamingbroccoli.net/
MM252
MM211
Passport Plus w/Spool Gun
TA185
Miller 125c Plasma 120v
O/A set
SO 2020 Bender
You can call me Bacchus
Comment
-
Well, I decided to put high leg on B phase, white in cord. I saw elsewhere that red is unused for single phase. Meaning that if it has any sensitivity to high leg on A, white must be acceptable. I can't see Miller making equipment that can't be connected to center tapped deltas via single phase.
Thanks for all the replies.
Comment
-
Delta 120/208/240 Three phase is 240 balanced on three phase. 240 single phase is available from any phase 120 single phase is available from 2 legs to neutral. 208 single phase is available from the high leg to neutral.Dynasty 280DX
Bobcat 250
MM252
Spool gun
Twentieth Century 295
Twentieth Century 295 AC
Marquette spot welder
Smith torches
Comment
-
Originally posted by WillieB View PostDelta 120/208/240 Three phase is 240 balanced on three phase. 240 single phase is available from any phase 120 single phase is available from 2 legs to neutral. 208 single phase is available from the high leg to neutral.
Originally posted by WillieB View PostIf it works on three phase, why not use three phase?
It is hooked up and working at 230V 3 phase connection settings.
Thanks again everyone!
Comment
-
Does the welder connect to neutral? If it does it is the first I've seen connected to neutral. Without neutral there is no high leg. Delta is three transformer windings connected in a triangle diagram. The wild leg or 208 is neutral to the opposite corner of said triangle. Your welder doesn't know about 208.Dynasty 280DX