  • ehofer1
    started a topic What size wire for 220 circuit for Miller 211

    What size wire for 220 circuit for Miller 211

    I'm getting the miller 211 and I need to wire in a 220 outlet for it. I need to know what size wire to use. Its about a 50' run Thanks

  • Bob Miller
    replied
    252 Manual

    I just looked in my 252 manual(page 20, sec. 5-12):
    Input voltage 230
    Input amps @ rated output 46
    Max recommended fuse in amps. time delay 50 amps
    normal operating 60 amps
    I don't know where a circuit breaker fits in here, but my guess is 50 amps.

    Min Conductor size AWG 8ga.
    Max conductor length 127 ft.
    Min ground size AWG 10ga.

    That said I have two store-bought extention cords both have Nema 6-50 ends,
    one is 2-8/1-10 and the other is 3/8.

    In the end I like the idea of 6ga. from a 50 amp breaker. Room to grow.

    Good Luck,
    Bob
    Last edited by Bob Miller; 06-19-2014, 10:51 AM. Reason: add word

    Leave a comment:


  • Bob Miller
    replied
    252 Manual

    I just looked in my 252 manual(page 20, sec. 5-12):
    Input voltage 230
    Input amps @ rated output 46
    Max recommended fuse in amps. time delay 50 amps
    normal operating 60 amps
    I don't where a circuit breaker fits in here, but my guess is 50 amps.

    Min Conductor size AWG 8ga.
    Max conductor length 127 ft.
    Min ground size AWG 10ga.

    That said I have two store-bought extention cords both have Nema 6-50 ends,
    one is 2-8/1-10 and the other is 3/8.

    In the end I like the idea of 6ga. from a 50 amp breaker. Room to grow.

    Leave a comment:


  • diyweldingplans
    replied
    I wrote a blog post about how to make an extension cord for the Miller 211 in March.

    Check out the site below and it should answer your questions. I used 8 gauge 3 wire and it was 65 feet long. I have never had a problem with it and have had it for almost 2 years (blog post came much later of course. )

    https://www.diyweldingplans.com/diy-...ord-diy-style/

    Leave a comment:


  • 1_old_man
    replied
    It would be difficult to immagine an inspector giving his approval to a 30 amp circuit using 14 gauge wire. Generally a circuit using 14 gauge wire is limited to 15 amps, and 12 gauge wire for 20 amp circuits, 10 for 30, and so on. Remember, the breaker is there to protect the wire, not the end user. Never skimp on wire, it is false economy. Besides, no one really likes the smell of their shop burning to the ground.

    Leave a comment:


  • Broccoli1
    replied
    Originally posted by Castiron View Post
    I don't believe #12 wire should be on a 50 amp breaker, and I don't think it's good for over 20 amp breaker but not sure.

    I just wired mine with #8 as I will probably get get something bigger down the road.

    Breaking the above mentioned rule, I did wire a 110 outlet onto one of the legs in the box so I don't have to run and additional ext. chord for the grinders.
    It's muddy for sure on this BUT it is allowable under certain circumstances.
    Even the Miller manual has 14g wire on a 30amp as minimum wiring if you follow the NEC art 630 guidelines.

    As Sberry mentioned the manual causes lots of confusion- that's why he stated 10g 30amp is a really good fit. Doesn't break the bank on wire costs and easy to work with.

    Leave a comment:


  • Castiron
    replied
    I don't believe #12 wire should be on a 50 amp breaker, and I don't think it's good for over 20 amp breaker but not sure.

    I just wired mine with #8 as I will probably get get something bigger down the road.

    Breaking the above mentioned rule, I did wire a 110 outlet onto one of the legs in the box so I don't have to run and additional ext. chord for the grinders.

    Leave a comment:


  • BD1
    replied
    I would run #6. That way when you upgrade you will have large enough wire. Price the difference between # 6 and 8

    Leave a comment:


  • cope
    replied
    Originally posted by bigtow30t View Post
    I ran mine off of 75' 8 gage wire and a 40 amp breaker. I think the book called for a 50 amp breaker
    My MM210 only calls for a 40 amp breaker.

    Leave a comment:


  • bigtow30t
    replied
    I ran mine off of 75' 8 gage wire and a 40 amp breaker. I think the book called for a 50 amp breaker

    Leave a comment:


  • Sberry
    replied
    The manual is confusing at best. Ignore the 14 and 30,,, with a wire 12 or better you can breaker this machine to 50A,,, but my tailor made circuit for one is 10/30.

    Leave a comment:


  • 1_old_man
    replied
    8 AWG with a 40 amp breaker because the machine draws almost 30 amps.

    Leave a comment:


  • raferguson
    replied
    Manual

    Originally posted by ehofer1 View Post
    I'm getting the miller 211 and I need to wire in a 220 outlet for it. I need to know what size wire to use. Its about a 50' run Thanks
    The manual should answer that question. It can be downloaded from the resources link at the top of the page.

    Richard

    Leave a comment:


  • Cgotto6
    replied
    This has been discussed many times. You will find lots of info by searching.