My old air compressor does not start all the time. Always used to work. Electric, 240v. When you flip the switch to on it sometimes hums (won't turn over). If you turn it off & rotate the motor sometimes you can get it to start. I'm not sure if rotating the motor has anything to do with it or just the on/off action. Checked all wiring connections which are o/k. Maybe the capacitor? If so how do I check it & where would I get one. I am upgrading anyway but wanted to sell this one rather than scrap it.
Announcement
Collapse
No announcement yet.
air compressor problem (electrical)
Collapse
X
-
air compressor problem (electrical)
MM250
Trailblazer 250g
22a feeder
Lincoln ac/dc 225
Victor O/A
MM200 black face
Whitney 30 ton hydraulic punch
Lown 1/8x 36" power roller
Arco roto-phase model M
Vectrax 7x12 band saw
Miller spectrum 875
30a spoolgun w/wc-24
Syncrowave 250
RCCS-14Tags: None
-
first thing to do is to check your voltage coming in to the pressure switch next check the voltage leaving the switch at the wires going to the motor. if the voltage going to the motor is within spec then there is a very good cance that the rotary switch inside the motor is faulty. unless you are familiar with electric motors you should take the motor to a re-wind or motor repair shop. if it is the switch it may not be too expensive. if you have aproblem in the windings a new motor would probably be cheaper.
hope this helps
larry
-
Capacitors dry out over time, sounds like yours has. Take it to the local motor repair shop and they'll sell you a new one for around ten bucks.
By spinning the motor to start it you're inducing the phase shift that the capacitor normally would.
Oldtimer's advice is sound, it could be the centrifugal switch but I'd suspect the cap first...
Steve the electrician...Miller Diversion 165
1966 Bridgeport Mill
Leblond 15x 35 Regal Servoshift lathe
Solberga SE 1425 Drill Press
Bigass Bandsaw
Hydraulic press
small surface grinder
Belt sander
Tons of grinders and hand tools
Knife edge Balancing rollers
Heat and AC in the garage
Jags and racing Triumphs
Comment
-
Mark Lindquist
Pump supply companys are a good resource for capacitors. You will need to know if their start or run caps as start are usually dry and run filled with fluid for continous operation. If This doesn't fix the problem and the centrifugal switch is ok then most likely the start winding has been comprimised.
Comment
-
Had the same problem with our bansaw a few weeks ago. Turn the motor a bit & it would usually take off. Took motor apart & filed the points on the start switch & it hasn't missed a beat since. Check the simple things first before you assume the worst. Good luck with it & keep us posted on what you find.252 Miller Mig
180 Synchrowave
R - 45 Milling Machine
Kingston 1100 Lathe
Miller 2050 Plasma Cutter
Comment
-
Check the unloader...
Another possibility might be the compressor unloader.. if it sticks... the motor may not be able to start under load... so is possible that it is not electrical at all..
just a thought
Heiti.
*******************************************
The more you know, The better you know, How little you know
“The bitterness of poor quality remains long after the sweetness of low price is forgotten”
Buy the best tools you can afford.. Learn to use them to the best of your ability.. and take care of them...
My Blue Stuff:
Dynasty 350DX Tigrunner
Dynasty 200DX
Millermatic 350P w/25ft Alumapro & 30A
Millermatic 200
TONS of Non-Blue Equip, plus CNC Mill, Lathes & a Plasmacam w/ PowerMax-1000
Comment
-
You got some good info here. Checking applied voltage is sometimes a misunderstood thing. You need to check voltage at the time the compressor is trying to start. You can get 240 volts through headphone wires but they can't carry the current to start a compressor. Most compressors use start capacitors as opposed to run caps. Start caps are cheap. Any HVAC supply will carry these. If the start switch is unavailable, it can be replaced with a solid state relay in conjunction with the existing capacitorsNick
Miller 252 Mig
Miller Cricket XL
Millermatic 150 Mig
Miller Syncrowave 200 Tig
2-O/A outfits
Jet Lathe and Mill
Jet 7x12 horz/vert band saw
DeWalt Multi Cutter metal saw
Century 50 Amp Plasma Cutter
20 ton electric/hydraulic vertical press
Propane Forge
60" X 60" router/plasma table
www.youtube.com/watch?v=jTu7wicVCmQ
Vist my site: www.nixstuff.com
and check out some of my ironwork and other stuff
Comment
-
Didn't read through all of the posts, but did you consider a bad bearing in the pump or motor?
PS: Glad to see Heti is still around!
Hank...from the Gadget Garage
Millermatic 210 w/3035, BWE
Handler 210 w/DP3035
TA185TSW
Victor O/A "J" series, SuperRange
Comment
-
Thanks for all the replies. Going to pickup my new air compressor today so this will most likely get stuck in the corner for a little bit. I'll let ya'll know what I find. Thanks.MM250
Trailblazer 250g
22a feeder
Lincoln ac/dc 225
Victor O/A
MM200 black face
Whitney 30 ton hydraulic punch
Lown 1/8x 36" power roller
Arco roto-phase model M
Vectrax 7x12 band saw
Miller spectrum 875
30a spoolgun w/wc-24
Syncrowave 250
RCCS-14
Comment
Comment