Originally posted by Fishy Jim
View Post
First, he's wrong about the receptacles not being allowed to be rated for more than the wiring/breakers. After all, a welding machine that draws 19.5A still comes with a 50A plug, and you can run it from #12 wire and a 30A breaker. BUT, there may be local codes which he might be enforcing. But some people worry about a future danger than someone might see a 50A receptacle and put it a 50A breaker without checking the amapcity of the wires in between. All you can do is ask him for a Code reference, but do so very politely and stay on his good side.
Article 455 is all about phase converters. Skimming through it, I see a few things worth noting to your specific application, but I accept no liability if I overlooked something, of course:
455.6 (B) says the manufactured phase shall be consistantly marked in all accessible locations.
455.8 says you have to have an all-pole disconnect within sight of the phase converter.
455.10 says to follow the table in 430.12 (Motors) for sizing the terminal housing of the phase converter.